Change Range for SEN0244 TDS Sensor Meter?

userHead AJGraham 2022-10-14 02:41:09 1631 Views1 Replies

Hey, is there any way to change the calibration of the sensor to read from 500PPM to 1500PPM?

 

I understand out of the box it's supposed to be from 0-1000 but for hydroponic applications 500-1500 is much more useful. I'm not looking to expand the range but shift the calculation. I have a separate PPM meter I can use to help me with my calibration, but I just want to know where/what I should change to affect this.

2023-02-22 16:52:47

Hi

Gravity: Analog TDS Sensor/ Meter for Arduino(SKU: SEN0244) is a pure analog sensor, with voltage output 0V to 2.3V from 0 to 1000PPM. Which means that the measurement range is fixed by hardware.

I'm sorry that you can not measure 1500PPM because the operational amplifiers on board can not output that voltage.

userHeadPic NeloKin